OK electricians

nowires

Well-Known Member
Joined
Jul 20, 2008
Messages
3,669
Location
Baring
OK electrician guys I am totally confused. But have also learned a lot. I just can’t get the math to work out
So here is the problem
6 - #6 2 / 220 50 amp circuits
3 - #8 1 / 220 40 amp circuit
3 - #10 grounds
So I have over 6 conductors so that put me in the 70% fill of conduit. I did the math and came up with 2.11 square inches. I am coming up with 2“ conduit

Is this right. According to the conduit fill chart I should be able to use 1.25†conduit

Any help would be cool
 
1 1/4 is what I came up with for the min. size. Are you planning on running EMT to the box's/device from your panel?
 
Last edited:
EMT is sufficient ground no need to throw your money away just have the device pigtailed to the box. We only pull grounds when its spec'd in pipe or if we had to use flex somewhere.
 
That is what I was figuring. The thing that threw me was the amount of conductors in the pipe and the fill rate. According to NEC I can only fill the pipe 70%. Is that right. I will have 9 conductors.
 
it all depends on the calc and pipe size and derating of wire maybe a little more info would help how long is the run and what you are doing?
:beer:
and 50 amp you can get away at # 8 thhhn if its not a long distance or draw under 50 amps
 
Last edited:
it all depends on the calc and pipe size and derating of wire maybe a little more info would help how long is the run and what you are doing?
:beer:
and 50 amp you can get away at # 8 thhhn if its not a long distance or draw under 50 amps

Here are the runs
1 50 amp for plasma cutter 35 ft run
2 50 amp for Air compressor 58 ft run
3 40 amp welder 72 ft run

The plasma I am going to draw all of that and will be for extended time periods on a CNC table
The air compressor is a 5 HP motor pulls 28 amps, but the manufacture recommends a 50 amp breaker
Welder I was already planning on #8 and 40 amp breaker
 
Pipe fill is based on 40 percent fill,any more than that and it gets harder to pull with the more bends you have
 
If you plan on expanding bumping it to 70% to save a buck it will bite you.

If your pinching pennies on conduit price, oversize it with the thought of expansion and run it in PVC. Take your time and make it look nice. Your going to need a grounding conductor. You'll be buying ground for pig tails anyways....

and so you know, 250.122C all you need is one #10 for all those circuits, as long as they are in the same conduit.

To each his own. If I was bidding a job I'd do minimum, if it was my place with thought of expansion... which almost always happens... I'd oversize.
 